| ▲ | sophacles an hour ago | |||||||
A solar panel is 4 feet or so on the long side. Theres 250+ of them in a string 1/4 mile long.... at 48 V/panel, you get to 12KV. even if it's topped out at 10A thats still 120KW... you need a hefty cable to carry that panel to panel. Which is the core of the point I was making. | ||||||||
| ▲ | cogman10 an hour ago | parent [-] | |||||||
Amps determine how hefty a cable needs to be, not volts. Volts mostly determine how thick the insulation needs to be. 14 gauge wire is basically all you need to carry 10A safely for an extended period of time regardless the voltage. It doesn't matter that you are carrying 120KW. The proof of this is in EV charge cables. Those bad boys can carry up to 350kW. Yet the cables are often thinner than you might expect. How do they do this? It's by using high voltages (around 900V) which cuts back the amps to around 300->400. Tesla's chargers peak (or used to) around 600V which has required them to have much beefier cables to handle the high current. | ||||||||
| ||||||||